HMI Pad Forums Main Forums ScadaMobile Support an error was found in received data

This topic contains 3 replies, has 2 voices, and was last updated by  Rossi 4 years, 4 months ago. This post has been viewed 1474 times

Viewing 4 posts - 1 through 4 (of 4 total)
  • Author
    Posts
  • #21479

    Rossi
    Participant

      Hello
      I have a problem.
      i need a new simatic controller:
      S7 1200 CPU 1214C 6ES7214-1BG40-0XB0

      the problem is: the scada mobile app connected not with the controller!
      Scada mobile write: An error was found in received data

      The source file is ok! i connect with the same file a other controller.

      Please help me.

      Thank you

      Best regards

      #21482

      Rossi
      Participant

        Now:
        I try to connect the new (simatic S7 1200 CPU 1214C 6ES7214-1BG40-0XB0) controller with the new firmware V4.0 (see the picture)
        I think the new firmware v4.0 on the controller is the problem.

        I use a source file it works on a simatic controller with firmware V3.0 but not on a controller with V4.0

        What do you think ?

        #21558

        John
        Keymaster

          Please try this. In TIA, under the properties for the CPU project, select “Protection”, there is an option for “Permit access with PUT/GET communications with remote partner…”. Note that you may need to scroll down to see that option.

          This should solve the issue.

          #21614

          Rossi
          Participant

            Great
            Thank you

          Viewing 4 posts - 1 through 4 (of 4 total)